Abby's Guide to Outdoor Power Equipment (Lawn Mowers, Snow Blowers, Chain Saws and more)
Username Password
Discussions Reviews More Guides
Abby’s Guide > Outdoor Power Equipment (Lawn Mowers, Snow Blowers, Chain Saws and more) > Discussions > Portable Generator Question

Outdoor Power Equipment (Lawn Mowers, Snow Blowers, Chain Saws and more) Discussions

Search For:
borat


Joined: Nov 10, 2007
Points: 2692

Portable Generator Question
Original Message   Jun 5, 2013 5:25 pm
For the last few weeks, I've been using the 2000 watt, Hyundai inverter generator at camp to provide electricity in light load applications.  Basically a 42" LED LCD TV, a Bell Receiver and a couple compact flourescent lights.   Less than 300 watts in total.   Initially I had just back fed the generator into the camp using a 12 ga. 50' extension cord.   After discovering that supplying that outlet also supplied limited power to the garage, I decided to try relocating the generator the 110 ft. or so from the camp to the garage.  I back fed the extension cord into an outlet at the garage and it powers all of the same circuits as the outlet on the camp did. 

The main power line from the garage to the camp is large diameter Tek cable (00 or 2/0) and is rated for around 195 amps so resistance should be minimal.   There is a very short eight feet of 14 ga. wire from the outlet to the main fuse box which controls the power from the large diesel generator to the main power line.  Now that I've explained the physical set up, my question is whether or not the additional distance of 120 feet or so of heavy wire transmission would put more demand on the small generator? 

The reason I ask is that I noticed what seemed to be a slight increase in fuel consumption with the exact same load.  Can't say for sure because I've only taken one fuel consumption reading from the new location. The fuel consumpiton variance was minimal.  I was getting a spectacular consistent 3 hrs./litre of fuel with the generator feeding directly into the camp.  The new location gave me a measurement of 2.79 hrs./litre.  

I know the numbers are insignificant and might just be a measurement variance, however, I'm still curious.  Does increasing the distance from the generator, despite the line having minimal resistance, increase demand on the generator?     
This message was modified Jun 15, 2013 by borat
Replies: 1 - 10 of 13NextNext page of topicsAllView as Outline
mkd55


Location: wisconsin
Joined: Dec 16, 2005
Points: 155

Re: Portable Generator Question
Reply #1   Jun 5, 2013 6:04 pm
the longer the power cord the more voltage drop at the connection. the shorter the run the less voltage drop.  If the generator is governed by rpm (a set rpm speed) only and not load than the voltage drop or loss could be measured with a multitester at the connection point on the end of the cord. if the rpm is governed by load then to supply the same voltage at a longer run  the engine  would need to increase rpm. the increase in rpm may be the reason for the increase of fuel consumtion.
This message was modified Jun 5, 2013 by mkd55
borat


Joined: Nov 10, 2007
Points: 2692

Re: Portable Generator Question
Reply #2   Jun 5, 2013 7:16 pm
Thanks for that.

Being that it's an inverter generator, I'll have to pull out the Sirometer and take some rpm readings at both locations.   It will be interesting to see what the results are. 

Not that I'm too concerned about the difference in fuel consumption.  The generator is extremely efficient for light load applications and the variance is minimal.

 
borat


Joined: Nov 10, 2007
Points: 2692

Re: Portable Generator Question
Reply #3   Jun 15, 2013 10:10 am
I did a couple experiments with the Hyundai generator.  Took rpm readings from the plug in location at the garage and hauled it down down for readings at the camp.  No difference in rpm under the same load conditons.  So,  I thought that maybe the six foot exhaust extension I put on it while at the garage location might have compromised engine efficiency by possibly increasing back pressure.  Did tests with and without the extension.  No difference. 

With those possibilities ruled out, I focused on the fuel measurement accuracy.  In the past, I'd fill a  one litre oil bottle to what I thought would be a litre of fuel.  This isn't the best method for real fuel measurement so I bought a one litre funnel calibrated in both metric and imperial measurements.   It's a very functional device with a handle on the side and a valve on the bottom of the funnel to hold the contents until it's time to empty it.  I just clamp the handle in a vice, put a one litre bottle under it and fill it often enough to fill the generator.  Anything left over is re-measured in the funnel. 

Bottom line is that my measurements were off.   Prior to getting the measuring funnel, I was over-filling the litre bottle.  Now with more accurate measuring I can say that I'm getting 2.20 hours to a litre of fuel under light load (500 watts or less). 

Another issue I was having with this generator was oil accumulating at the base.  I opened up the shell looking for an engine leak (i.e. valve cover)  and found everything nice and dry.   I then followed the crank case ventilation tube to the air intake housing for the carb.  Everything was good there until I pulled the air filtre and noticed that the tube terminates at the bottom of the housing and was inserted into a piece of sponge to collect oil residue.  The sponge was fully saturated and the oil was seeping from a seam at the bottom of the air intake housing.  I've concluded that the problem was oil over-fill.   The machine comes with a small oil bottle (.47 litre) that I refilled when I'd do the oil changes.  Problem was that I was over-filling the small bottle thus over-filling the generator.   The volume of the crank case doesn't tolerate much of a variance in oil.  Probably around one oz.   Filling beyond that will cause oil to be forced out the crank case ventilation tube.   When filling the crank case, I was under the impression that a proper fill would be to the top of the threads on the oil fill hole.  That's incorrect.  A proper fill is just to the bottom of the hole. 

Now that I have that figured out, oil seepage has stopped completely and I'm more than pleased with this generator.   It starts and runs great, returns excellent fuel economy and from the garage, I can't hear it.  Only time will tell how long it will hold up.  From what I've seen, it looks to be well built and other than being a bit heavy, is an excellent value for the money.  Walmart sells it for $699.00 CAD regular price and occasionally on sale for much less.   That's half the price of a Honda EU2000 and the Hyundai actually generates 2000 watts continuous, while the Honda generates 1600 watts continuous.   Not saying the Hyundai is in the same class as the Honda or Yamaha.  However, if it holds up half as long, it's a good buy.  Anything beyond that is a bonus.           
This message was modified Jun 15, 2013 by borat
hirschallan


If it aint broke don't fix it !!


Location: Northern Hills of NY
Joined: Aug 25, 2005
Points: 327

Re: Portable Generator Question
Reply #4   Jun 16, 2013 2:01 am
borat wrote:


Bottom line is that my measurements were off.   Prior to getting the measuring funnel, I was over-filling the litre bottle.  Now with more accurate measuring I can say that I'm getting 2.20 hours to a litre of fuel under light load (500 watts or less).            


BORAT Just want to make sure I'm following you correctly. When you say "2.20 hours" do you mean 2.20 hours which = 2 hours and 12 minutes OR are you saying 2 hours 20 minutes??

borat


Joined: Nov 10, 2007
Points: 2692

Re: Portable Generator Question
Reply #5   Jun 16, 2013 12:32 pm
I'm back in town now and don't have the figures with me.  If I recall correctly, I measured 8.7 hours run time on close to 4 liters of fuel.  That works out to 2.175 hours per litre wich I rounded off to 2.2 hrs/liter.  Which is approx. 2 hrs. 12 minutes.  

I know I'm pretty much splitting hairs now but I suspect that my measurements are a bit conservative.  During the 8.7 hours, some of it was under 1000 to 1500 watts of load.  Maybe a total of ten minutes or so.  In addition to that, when I refueled I probably squeezed in a few more oz. than normal, which would skew measurements a bit.   I plan to try to be as consistently exact as possible when refueling to get an accurate base line.  However, I'm confident that under my normal light load of 500 watts or less, I should see 2.5 hours per  litre.   Which is considerably better than the 1 litre of diesel fuel per hour  I was burning to run the Kubota powered 6K watt  generator.  

If the Hyundai holds up for five years or more, it will easily pay for itself in fuel savings as well as reducing oil change costs.   I go from using 4.6 litres of oil for the diesel to less than half a litre for the Hyundai and the recommended hourly duration for the Hyundai is the same as the 100 hrs. I was changing the diesel at.  That equates to almost ten oil changes for the Hyundai for each Kubota oil change.   At approx. $30.00 for oil and filter for the diesel oil change, it doesn't take too long for the Hyundai to pay for itself providing it lasts.   Considering that most of it's life will be spent  loafing along at approx 2000 rpm, in a clean environment, I suspect that it should hold up reasonably well with proper maintenance.  

Reducing fuel and oil consumption is also ecologically much more friendly.  I like that.

Overall I'm pretty happy with this little generator.   When we have it running  up at the garage location, it's so quiet that we forget that we've got a generator running.  Very pleasant indeed.  
This message was modified Jun 16, 2013 by borat
borat


Joined: Nov 10, 2007
Points: 2692

Re: Portable Generator Question
Reply #6   Jun 16, 2013 8:49 pm
Would anyone know approximately what the engine rpm operating range would be for an inverter generator?   I know the Hyundai's uppper engine rpm is 5500 at full load.  However, I'm a bit confused with the lower engine no load speed despite measuring it with the Sirometer.   I get strong readings at 1700 and 3400 rpm at no load.   My ears tell me that it's running pretty slow and I'm thinking 1700 rpm.   Would anyone know for sure what the lower no load rpm range is on inverter generators?
Paul7


Joined: Mar 12, 2007
Points: 452

Re: Portable Generator Question
Reply #7   Jun 17, 2013 2:04 am
I have a small Yamaha Inverter. I bought it used but recall getting the manual with it. I'll see if I can find it and post if I find anything in the specs.
borat


Joined: Nov 10, 2007
Points: 2692

Re: Portable Generator Question
Reply #8   Jun 17, 2013 9:15 am
Information on the lower rpm operating range for inverter generators is difficult to find. 

I've done a fair amount of searching and found a forum that had some good info on inverter generators.   I learned that inverter generators run at two speeds only "Eco" mode (low speed) and full load speed.   I was under the impression that inverter generators could regulate engine speed to suit load requirements.  That assumption was wrong.  When the demand on the generator exeeds the power being delivered in Eco mode, the generator opens to max throttle to meet the additional demand.  It was suggested that the lower rpm range is usually half of full load operating rpm.  If that's the case,  the Hyundai continous max. load rpm is 5000 rpm, accordingly lower rpm speed should be 2500 rpm.   I cannot confirm nor dispute this info. however, my rpm measurements tell me otherwise with the Hyundai being either 1700 rpm or 3400 rpm.    

Considering the prominence of electronic fuel injection in many small engines such as those found on late model ATVs, motorcycles etc. one has to question why this technology has not been integrated with inverter generators?  It would simple enough to "map" a sliding scale on the EFI to match engine rpms to generator demand.  Seems like a no-brainer to me.  The efficiency gains would be substantial.      
This message was modified Jun 17, 2013 by borat
robertcoats


Joined: Dec 12, 2011
Points: 39

Re: Portable Generator Question
Reply #9   Jun 18, 2013 8:29 am
borat wrote:
Considering the prominence of electronic fuel injection in many small engines such as those found on late model ATVs, motorcycles etc. one has to question why this technology has not been integrated with inverter generators?  It would simple enough to "map" a sliding scale on the EFI to match engine rpms to generator demand.  Seems like a no-brainer to me.  The efficiency gains would be substantial.      

One element electronic fuel-injection systems require is a battery or some source of power to energize the electronics before the engine can be started. Not a big deal on say a 3kw unit that already has electric start and has a battery, but for small portables (2.5kw and below) that are only recoil start, it could be a real engineering challenge. A battery (and electric start) adds significant weight too, and nobody in sales / marketing wants a portable generator to gain any weight.

With the issues carburetors have these days with ethanol fuels, there's little doubt fuel-injection will eventually work its way into small gas engines and power equipment. Hang on.

-Robert@Honda
Caveat: I work for Honda, but the preceding is my opinion alone.
borat


Joined: Nov 10, 2007
Points: 2692

Re: Portable Generator Question
Reply #10   Jun 18, 2013 9:21 am
Good points. 

Wouldn't take too much of a battery just to power the fuel injection until the generator kicked in and there wouldn't be a starter/solenoid involved to add weight.  I'd say it's probably not too far off in the future.
Replies: 1 - 10 of 13NextNext page of topicsAllView as Outline
Outdoor Power Equipment (Lawn Mowers, Snow Blowers, Chain Saws and more) Guide   •   Discussions  Reviews  
AbbysGuide.com   About Us   Terms of Use   Privacy Policy   Contact Us
Copyright 1998-2024 AbbysGuide.com. All rights reserved.